General Service Fire Alarm System Minerva T1008

General Service Fire Alarm System Minerva T1008

General Service Fire Alarm System Minerva T1008

Specification:

  • MCFA (Main Control Fire Alarm)
    • Equipment Fire Alarm Control Panel
    • Brand Minerva
    • Type T1008
    • Voltage 230VAC
    • Frequency 50Hz
    • Current 2A Class 1
  • Fire Alarm Sensor Smoke and Heat Detector
    • Equipment Smoke Detector
    • Brand Tyco
    • Type 601P-M Conventional
    • Product By Tyco Safety Product, UK
  • Break Glass and Call Point
    • Equipment Break Glass and Call Point
    • Brand Thorn Scurity
    • Switch Rating 2 Amps at 30vdc
    • Materials Front- PC/ABS

Error Issue:

  • Condition General Fault.
  • Some detector is not functioning.
  • Some Break Glass is not function.

Action Taken

  • Zone consist of:
    • Zone Location
    • Zone 1 Wheel House
    • Zone 2 Forecastle Deck
    • Zone 3 Second Deck
    • Zone 4 Main Deck
    • Zone 5 Emergency Generator
    • Zone 6 Bow Thruster Room
    • Zone 7 Engine Room
    • Zone 8 Steering Gear Room
  • Checking master fire alarm control device.
  • Checking all sensing device:
    • Smoke Detector
    • Heat Detector
    • Break Glass / Call Point.
  • Checking all Bell Alarm
  • Checking interconnection with other device.

Solution Resulting:

  • Checking on the detector, there is a malfunction with the following data:
    • Call Point / Break Glass 2 Unit
    • Heat Detector 2 Unit
The replacement has been done, using spare.
  • Some problems are the fault on the master control: the emergence of fault, this can we cope with the addition of the resistor in the end of the line and on some terminals that are not used or connected to external devices.
  • No problems on the device Alarm Bell, interconnection to the external device.

Documentation

Fire Alarm Control Panel, Minerva, T1008, 230VAC, 50Hz, 2A Class 1
Fire Alarm Control Panel, Minerva, T1008, 230VAC, 50Hz, 2A Class 1
Fire Alarm Control Panel Circuits
Fire Alarm Control Panel Circuits
Break Glass and Call Point, Thorn Scurity, 2 Amps at 30vdc, Front- PC/ABS
Break Glass and Call Point, Thorn Scurity, 2 Amps at 30vdc, Front- PC/ABS
Break Glass and Call Point, checking and repairing
Break Glass and Call Point, checking and repairing
Testing with smoke on smoke detector
Testing with smoke on smoke detector
Testing insulation, voltage and connection
Testing insulation, voltage and connection